No video

Leak Search Tips From Bert

  Рет қаралды 70,356

HVAC School

HVAC School

Күн бұрын

Bert explains some of his best leak search tips. We use his tips for leak detection at Kalos, and although leak detection can be intimidating for beginners, it absolutely MUST be done right.
Before you start any type of leak detection, you must confirm that the system is low on refrigerant. When you confirm that a system has a low refrigerant charge, you then need to estimate how low the charge is so that you can get an idea of the leak's size. Then, you can find the leak.
The visual inspection comes first. You will want to look at common problem areas often touched by humans, such as joints. In many cases, the refrigerant or oil will leave spots or a trail where it has leaked; shiny pipes may look dull or wet. Check for discoloration of oil on top of the water in the drain pan as well. Leaks may be larger and faster on the high side of the system, so try to pinpoint the exact area when you have leaks at the outdoor unit. You'll also want to check the capillary tubes, look for oil lines, and watch out for rust on the accumulator.
After you find a spot visually, you can bring out your electronic leak detector (heated diode, infrared, or ultrasonic). Know your electronic leak detector's limitations; otherwise, you might unknowingly pick up false positives. Move the leak detector from top to bottom; if you start from the bottom and go up, you might get a false point because the refrigerant is heavier than air and sinks. Once you get a hit, do a bit more leak detection before going back and confirming that you still have the hit. Then, you can use a liquid leak reactant on the possible leak area; bubbles will constantly form over the leak. (However, it's harder to use bubbles to confirm leaks between fins; in those cases, make sure you confirm it with your detector by going back several times.)
Evaluate the leak to see if you have a leaky joint, if you can potentially repair the leak, or if you can take another course of action. Sometimes, you may need to get access to the chase to assess the line set for leaks. Schrader leaks are possible, but they are often not the main culprit of major leaks, so keep going through the entire system after you find one leak (or get a hit on the Schrader ports). Confirm Schrader core leaks with bubbles, too. Leaky refrigerant caps hold oil, so check those if you get a hit on the refrigerant caps.
After you find and evaluate the leak, gather all the information you need from the system and the customer to determine the next course of action. Check for warranty information and see if labor and parts are covered. If you do a replacement, you need to think about replacing the filter-drier and recovering the refrigerant from the system.
If you still can't find the leak after following all of these steps, talk to the customer about your options, including quoting and performing a line isolation test.
Read all the tech tips, take the quizzes, and find our handy calculators at www.hvacrschoo....

Пікірлер: 77
@garrygraves3848
@garrygraves3848 2 жыл бұрын
I'm new at this and I definitely got alot out of it !☺
@jproper
@jproper 2 жыл бұрын
Been in the trade going on 7 years and I always pick up something new from your videos. Gotta keep that student mindset always!
@user-hj5le6lo9w
@user-hj5le6lo9w Жыл бұрын
Been in hvac over 25 yrs and got a lot of info from this video. Bert obviously has a great deal of experience and takes pride in his craft. Thanks for sharing Bert!
@michaellake5550
@michaellake5550 2 жыл бұрын
I was in the HVAC field for over 50 years! I've seen many changes. We would troubleshoot leaks with the bubble method, didn't have the fancy stuff till later. Amazing how the trade equipment has improved. Great video. I miss the trade but still do some refrigeration work occasionally. I'm knocking on 80 yrs old. You guys have fun and I'll enjoy my well earned retirement. Better to be certain that guess!
@wayneh150
@wayneh150 2 жыл бұрын
I want to learn HVAC air conditioning and have been binge watching your videos They are really good
@baitcasterdisaster8981
@baitcasterdisaster8981 2 жыл бұрын
Awesome video Bert! Very thorough and you covered everything I hoped you would. From the way to spray on Big Blu slowly so you don’t create a lot of bubbles, starting with a visual inspection looking for oil trails FIRST. I like the way you stressed to confirm several times so you don’t charge the customer for an unnecessary repair and have to return because you got it wrong the first time. Always go over the spot multiple times with your leak detector and make sure you get a hit each time, then confirm with bubbles whenever possible. It’s also a pet peeve of mine when other technicians at my company add 6 pounds of refrigerant and say it was a leaking schrader valve because they couldn’t find the leak or they were just too lazy to find if. I’m usually the one that has to go behind them and find the leak because I do it right the first time and I take a lot of pride in my work. On a side note, I’ve had really good results using an infrared Inficon D-Tek 3 leak detector but I also own a heated diode Fieldpiece as well.
@povoljan13
@povoljan13 Жыл бұрын
Do you like the heated diode better or the infrared?
@rjlinnovations1516
@rjlinnovations1516 2 жыл бұрын
Excellent tutorial. Easy to follow and I was already retired in this trade but there is still room for learning new technique in your video. Good job 👍
@dylandrymond3839
@dylandrymond3839 2 жыл бұрын
Well done. Very informative. The HVAC School is one of the best places to go for HVAC training. Thanks Bert.
@kevinkrug466
@kevinkrug466 2 жыл бұрын
I wish this was around in 2013 when I started doing AC because I learned all this points the hard way. good job as usual
@jessicaeagan3165
@jessicaeagan3165 2 жыл бұрын
Another great video from Bert. Thank you for helping us continue to use best practices in the field.
@terrygrant8126
@terrygrant8126 2 жыл бұрын
That was great!......Hands on experience sure beats classroom discussion every time!....thank you friends!
@jericosha2842
@jericosha2842 2 жыл бұрын
Perfect explanation. Burt always does a great job presenting.
@Choirboyjr11
@Choirboyjr11 2 жыл бұрын
Thanks for the video! Never thought about condensation heading differently because of oil. Brilliant
@GOODNEWSHVAC
@GOODNEWSHVAC Ай бұрын
great video thx Bert!
@waynemiles7027
@waynemiles7027 2 жыл бұрын
Best way to check for leaks at schraider valves is to carry two spare caps in your tool bag and drill a small hole in them and then place them over the schraider valves and dab some bubbles on them and check, it works every time. This way you keep the solution off the valves.
@dreadfuljason4166
@dreadfuljason4166 2 ай бұрын
I wish I could shake your hand, that’s the best idea.
@heatingairservices8708
@heatingairservices8708 8 күн бұрын
awesome tutorial I also Have both the same exact leak detectors you show the H 10 is my older one but still use but batteries are shot so must find an plug in ...& the CPS leak seeker & love both tools but the H 10 finds R 22 leaks quick & easy but have to turn up the heat on 410 & back down for 22 .. my CPS also works great & is my quick no power cord needed tool of choice 90 % of the time
@sermore77
@sermore77 2 жыл бұрын
Bert congrats well done keep them coming💪🏼👨🏻‍🔧👍🏼
@Will_G302
@Will_G302 2 жыл бұрын
Thank you for the great info! its nice to have a refresher especially getting back into the busy ac season.
@vicgewondjan647
@vicgewondjan647 2 жыл бұрын
Thanks Bert! Well said...
@zesty2023
@zesty2023 2 жыл бұрын
I will never go back from my ultra-sonic leak detector, thanks Craig.
@seek3n
@seek3n Жыл бұрын
Sucha good workspace where these systems installed.
@vicgewondjan647
@vicgewondjan647 Жыл бұрын
Thanks Bert! Good stuff!!!!
@jathanbooher1465
@jathanbooher1465 4 ай бұрын
Appreciate the tips!
@grandmazinger73
@grandmazinger73 3 ай бұрын
Thanks for the great video, needless to say it's very educational video. I'm a homeowner and my system has leak in the low pressure line going into the compressor. I discover a large stain of oil inside the attic where there is a brazed union. My question is, what should a technician do in this case to repair the system properly? Is the best practice to recover all the refrigerant, then make the repair, change the filter and finally add the refrigerant again? Or do I let the technician add the leak stopper in a can? I'm asking because I live in the south and I fell like no one wants to take the time to make the repairs properly. All the technicians want to do is to add the leak stopper in a can and I head this type of gas can end up damaging the compressor in the long run. I'm just looking for some advice. Thanks for the video, it was really helpful
@seshachary5580
@seshachary5580 5 ай бұрын
very educative . Thank you regards
@mohamadafravi1160
@mohamadafravi1160 2 жыл бұрын
Absolutely useful 👌👌👌👍👍👍
@timrob0420
@timrob0420 2 жыл бұрын
H10 is good, I just hate how often you have to mess with the calibration on it. Just got the Fieldpiece dr82 pretty excited about that
@stephenbell9324
@stephenbell9324 2 жыл бұрын
Dyes and a sonic are my weapons of choice. Always confirm with bubbles
@Taras-Nabad
@Taras-Nabad 2 жыл бұрын
Let me begin by saying your video was excellent. What happens now? Can you repair the leak? Is it cost prohibitive? I am surprised to see the A coil is so rusted on a Lennox system which I heard is the best. So after you spend so many hours and hundreds if not thousands of dollars, does it pay to fix an old system? Future leaks are possible, no? Am I missing something? Great video.
@TitaniumZX
@TitaniumZX 2 жыл бұрын
Great info...thanks!
@muhammadusamakhan5295
@muhammadusamakhan5295 2 жыл бұрын
thanks sir
@peterhodgkins6985
@peterhodgkins6985 2 жыл бұрын
Excellent!
@mikecorral2358
@mikecorral2358 2 жыл бұрын
Burts the man.
@UltraHydrophobiccoat
@UltraHydrophobiccoat 2 жыл бұрын
The H10 manual says once the low battery light is on it wouldn’t work. I found your H10 low battery light is on 😊
@DanO181919
@DanO181919 2 жыл бұрын
shray · dr valv
@allenheineck2359
@allenheineck2359 2 жыл бұрын
Not being able to pronounce what you're telling someone about is a huge pet peave of mine.
@frankmashione139
@frankmashione139 2 жыл бұрын
Good video
@H2OLIQUID1
@H2OLIQUID1 2 жыл бұрын
90% of the leaks I find, low side Schrader valve core stem. Folks miss it because they hook up their gauges and don't check there. 😆
@H2OLIQUID1
@H2OLIQUID1 2 жыл бұрын
Glad you went over that issue. Awesome video
@techvlad8736
@techvlad8736 2 жыл бұрын
You must be new in the HVAC field
@hodesto
@hodesto 2 жыл бұрын
Great video. Question I have is what percentage or amount of refrigerate has to be present in the system for a mechanical leak detector to work. At what point do you need to add refrigerate to a system to find a leak. Or do you never add to find a leak ? Great channel
@rayzerot
@rayzerot 2 жыл бұрын
For a system that is flat, the EPA allows you to pressurize a system with nitrogen and a small amount of R22 to perform leak searches. Otherwise it's illegal to add refrigerant to a flat system for the purposes of leak detection. I believe it's considered ok to add refrigerant to a system that still has charge though.
@bikerbobcat
@bikerbobcat 2 жыл бұрын
I love "also a dead rat. ...I know." Great video. Any thoughts on UV dyes? I've found a bunch with dye checks. Even found one with dye frozen in to the ice on the coil and was able to show the customer.
@user-li4ik9qs8c
@user-li4ik9qs8c 2 жыл бұрын
Hi, can we use the leak detector to find out leak in the old school deep freezer which has hidden pipes between foam and Aluminum layer? Thanks.
@austinbooger1999
@austinbooger1999 2 жыл бұрын
The people complaining about how Schrader is pronounced are the same people who leave the capacitor inside the box when replacing it. We all know what he is talking about, grow up and enjoy the free education.
@ralphpagan3371
@ralphpagan3371 2 ай бұрын
How long to find leak after adding dye to system.I had dye added three months ago and can’t find leak. What’s the next test ??
@LispyJesus
@LispyJesus Жыл бұрын
If the filter drier is inside the unit you can’t pump down? I’ve never heard this. I have had units that won’t pump down fully just figured some do some don’t.
@allenheineck2359
@allenheineck2359 2 жыл бұрын
I'll say it. Can we have more from Bryan? Bert leaves something to be desired.
@grashoprsmith
@grashoprsmith 2 жыл бұрын
I think both have their strengths
@allenheineck2359
@allenheineck2359 2 жыл бұрын
@@grashoprsmith Stray-der! Really, come on. His boss doesn't say it that way.
@rj.parker
@rj.parker 2 жыл бұрын
@@allenheineck2359 I understood him perfectly. Content is more valuable than a "Shray-der". The German pronunciation is closer to Bert's which must mean he is honoring the immigrant inventor, August and son George Schrader. Their company still exists and came up with the tire pressure monitoring system.
@ShiYushi
@ShiYushi Жыл бұрын
How do I know how much refrigerant was lost on the unit? I’m still learning about it
@andrewharless8668
@andrewharless8668 4 ай бұрын
I've only been doing it for about a year, but for me, It's once I recover all the refrigerant that I can use a scale to see how much was recovered. Just compare that to what the factory charge states on the data plate, and that figure minus what you recovered will give you the minimum it lost. Could be more though if the line set is longer and more than the factory charge was required.
@gaylefriedman3773
@gaylefriedman3773 11 ай бұрын
My main concern is that A/C Condenser is on a Roof? Worst Case Scenario! How can you du a check up?😮 Like walking up a 32 or 40 step ladder? The cheapest form of care for your A/C Unit!😢
@soleilsoleil8287
@soleilsoleil8287 2 жыл бұрын
Awesome
@grashoprsmith
@grashoprsmith 2 жыл бұрын
"Strader" this must be an inside joke or a Florida thing. I say this with kindness ❤️. Bert obviously knows his trade
@austinbooger1999
@austinbooger1999 2 жыл бұрын
genuine question. why does it matter how its pronounced when everyone knows exactly what he is talking about?
@grashoprsmith
@grashoprsmith 2 жыл бұрын
@@austinbooger1999 It doesn't.
@jimk.8783
@jimk.8783 Жыл бұрын
What about dye?
@noufalkilayil7713
@noufalkilayil7713 2 жыл бұрын
Thank you
@whitesheatingairappliancer7101
@whitesheatingairappliancer7101 2 жыл бұрын
Are you guys installing sight glass on residential units?
@rayzerot
@rayzerot 2 жыл бұрын
Sight glasses are completely unnecessary. A tech should be hooking up their gauges and temp clamps to properly diagnose.
@matthewodonnell1856
@matthewodonnell1856 2 жыл бұрын
Sight glasses are a good idea to have on a residential system. Put it as close to the TXV as possible. That way you can see if you have a full column of liquid going to the TXV. It obviously isn’t the only thing A tech would look at when diagnosing but it can be a helpful aide. You would still need to follow properly diagnostic procedures but I don’t understand why its “completely unnecessary”?
@gaylefriedman3773
@gaylefriedman3773 11 ай бұрын
If readers state they were in A/C for 25, 50, whatever, where do you work? Let this be known. If you're that great, let it be of knowledge!😅
@gaylefriedman3773
@gaylefriedman3773 11 ай бұрын
What's the purpose to keep an on going A/C Unit Problem? Just start New! Will Cost you More in the Long Run!😂
@vijayanathanstephen9308
@vijayanathanstephen9308 2 жыл бұрын
👍👍👍
@stephwaylonwells3218
@stephwaylonwells3218 2 жыл бұрын
👍
@landoe9580
@landoe9580 2 жыл бұрын
Ryobi? Really?
@realestateservicessaleshea99
@realestateservicessaleshea99 2 жыл бұрын
Can't wait for the line iso test? Thanks again for the videos! 🍺🍺🍺🥃🥃🎳⛳ Stay safe. Retired (werk'n)keyboard super tech. Wear your safety glasses!
@timrob0420
@timrob0420 2 жыл бұрын
Also, if leak is in evaporator for most part you replace the coil. So who cares where it’s at at that point lol
@babyking5763
@babyking5763 2 жыл бұрын
Could be on one of the U tubes on the edge of the coil, fixable.
@timrob0420
@timrob0420 2 жыл бұрын
@@babyking5763 if it’s under warranty it’s best just to replace the coil
@davidhenkel5500
@davidhenkel5500 Жыл бұрын
I compare leak detection to "DEXTER" he was a blood splatter analyst. Comps. Bleed oil
@kangaroogod
@kangaroogod 2 жыл бұрын
👍
Which Leak Detection Method is Best? Craig vs. Bryan Cage Fight
35:27
How to Line Isolation Test an AC System
9:45
HVAC School
Рет қаралды 39 М.
طردت النملة من المنزل😡 ماذا فعل؟🥲
00:25
Cool Tool SHORTS Arabic
Рет қаралды 23 МЛН
小丑把天使丢游泳池里#short #angel #clown
00:15
Super Beauty team
Рет қаралды 48 МЛН
Accumulator Facts & Tips
24:44
HVAC School
Рет қаралды 121 М.
Low Refrigerant? Freon Leak? Check This First!
7:02
Sam
Рет қаралды 431 М.
HVAC161 Condensing unit leak search Tips
13:34
Love2HVAC with Ty Branaman
Рет қаралды 8 М.
Goodman Heat Pump Low On Refrigerant!  Adding Leak Stop And Charging With R-410a!
12:43
Where to Find R-22 & R-410A LEAKS on AC Units! Top 10 Spots!
14:46
AC Service Tech LLC
Рет қаралды 199 М.
HVAC 159 Why evaporator coils leak (Fixed)
10:56
Love2HVAC with Ty Branaman
Рет қаралды 56 М.
Fieldpiece Leak Detectors
21:30
TruTech Tools, LTD
Рет қаралды 34 М.
How to Evacuate an AC system, Full Vacuum Procedure
27:35
HVAC School
Рет қаралды 1,2 МЛН
Capacitor and Hard Start Myths Busted
28:41
HVAC School
Рет қаралды 229 М.