Why some Single ovens can be plugged in some need to be wired in ?

  Рет қаралды 361,695

RuislipAppliances

RuislipAppliances

7 жыл бұрын

A Video Shot at Ruislip Appliances Ltd , 112-116 Pembroke Road Ruislip Manor Middx HA4 8NW , Telling you why some Single ovens can run on a 13amp Plug top but some single ovens need to be hard wired in. if your oven as a rule is below 3000w (3.0 KW) it can be plugged in above the 300w (3.0KW) you need to hard wire the oven into either a 20amp supply or a 32amp Supply.

Пікірлер: 98
@LateBarLondon
@LateBarLondon 3 жыл бұрын
Informative. Thanks. The point I took from this is that it's important to check whether the existing oven is plugged into the 13amp circuit or has a dedicated 30amp hard wired supply prior to buying a replacement oven.
@philpickering5189
@philpickering5189 Жыл бұрын
Great explanation and as you say probably the most common question asked
@leerice2829
@leerice2829 3 ай бұрын
Thanks for the clear and concise explanation
@qchupritam
@qchupritam 2 жыл бұрын
Thank you, very important information simplified!
@sahidsim
@sahidsim 2 жыл бұрын
Thank you. Made my life a lot easy. Now I know what kind of oven I need to buy.
@markandrews8437
@markandrews8437 6 жыл бұрын
Nicely explained and made sense cheers
@luisquijada9764
@luisquijada9764 2 жыл бұрын
Very good video clear my doubts at the end of the video.
@ashyclaret
@ashyclaret 5 жыл бұрын
Thanks,just what I needed!
@pratimamehta6195
@pratimamehta6195 3 жыл бұрын
Thanks for advice it was useful
@SquaddieSoul
@SquaddieSoul Жыл бұрын
Thank you, very helpful.
@jonkeilty3340
@jonkeilty3340 6 жыл бұрын
Thanks for advice
@bobb6587
@bobb6587 4 жыл бұрын
The best advise for oven installation ever
@user-zp2lv6yj9n
@user-zp2lv6yj9n 8 ай бұрын
Good information.
@jensschroder8214
@jensschroder8214 3 ай бұрын
10A is recommended for old and unknown Schuko sockets and plugs. Permanent 16A is only possible if the socket and plug are new, solide and from a good manufacturer. The French even allow 20A on the 2.5mm² wire.
@iiemerald4545
@iiemerald4545 3 жыл бұрын
Very informative. Is it ok to have a spur from the cooker connection to a socket to connect the cooker. Or can you cut off the plug and hardwire it to the cooker connector
@iangillatt9203
@iangillatt9203 4 жыл бұрын
Thank you
@PakFan786
@PakFan786 5 жыл бұрын
can you do a video on how to hard wiring a new neff oven
@Grahamgusbull
@Grahamgusbull 6 жыл бұрын
I will now sleep tonight,thanks!
@daveboddis6331
@daveboddis6331 2 жыл бұрын
I was always on the understanding that if an appliance DIDN'T come with a plug, it had to be wired in (Plug & Sockets regulation), irrespective of power rating?
@woktown
@woktown 6 жыл бұрын
i live inn a smal appartement inn Norway and i hav a problem wit the oven i plug it inn and after 1 minute the braker stops i have just the standard plug for norway i don haw nofing for the oven so i conet it to the wall outlet and the power of the apartment is un 230V in 16A i♦n 0,03A B16 help wat to do? and sory for my english.
@thewolfydragon1989
@thewolfydragon1989 3 жыл бұрын
So am. I right I can't get a pyrolytic oven that can be plugged straight in? Because I can't have hard wired due to renting. And the plug socket goes on the entire kitchen sockets. (the hob is hard wired but the oven is just a plug and housing said I have to pay them £300 for rewiring and not paying that when I rent)
@gedruxton871
@gedruxton871 3 жыл бұрын
My 2700 w oven is hardwired directly from its terminal to a 32a mcb at the board. I'm changing it for another cooker and giving the old one away. That person wants to connect a 1.5sqmm cable and plug and plug it into a 13a socket on his normal socket circuit. Is this safe /allowed?
@Makeithappen1986
@Makeithappen1986 5 жыл бұрын
so a cooker at 2850 w could be made part of a ring circuit then?
@tweetypie25
@tweetypie25 4 жыл бұрын
We have a Beko 2.3KW oven, can I supply this from the back of the Socket to a flex fused spur unit ( for isolation) The diouble socket is near to the oven but I would like to keep this socket free thus hard wiring into the back of the socket!! Cheers.
@wellifthemediasaysit
@wellifthemediasaysit 2 жыл бұрын
Hi, my current oven is hardwired in, to a 13amp circuit. My new oven is also 13 amp! So i can simply just isolate, and wire in the replacement?? cheers
@peterryan7827
@peterryan7827 3 жыл бұрын
We have to replace an oven, which is a double oven,, with a single cheaper version quickly, can we just hardwire that cable into to new oven,or is there an issue with fusing etc,
@patricbrown8721
@patricbrown8721 8 ай бұрын
So would you wire your built in ovens in 6mm flex if it's been connected to a 6mm cooker circuit
@user-zp2lv6yj9n
@user-zp2lv6yj9n 8 ай бұрын
Hence why my oven has an 13 amp plug and the hob above is hard wired wired into a 60 amp circuit .
@killianmmmoore
@killianmmmoore 4 жыл бұрын
What about the Spanish 25amp oven plug? Could uk and ireland adopt that?
@hellblazer1980
@hellblazer1980 2 жыл бұрын
Can you let me know what a flavel milano ml61cds needs, can it be plugged in? I can't find the rating plate or whatever.
@designertjp-utube
@designertjp-utube 4 жыл бұрын
Hi! i live in The States. Does this mean my 20 amp circuit breaker in my 110 volt AC home can run this 3000w 13amp beauty oven of yours? I'm also assuming there's a switch in the back to back down the voltage from U.K. 220 to USA 110 volt.
@trishalove6745
@trishalove6745 7 ай бұрын
can i wire a cooker hob on its own to a plug it state 32 hardwired so what do I do please
@puttladla
@puttladla 2 жыл бұрын
My oven got 5 core cable.. how to fit into 3 terminal Uk plug (moffit brand)
@deborahwebb7544
@deborahwebb7544 3 жыл бұрын
Can a plug in oven be converted to hard wire?
@thebohemianwonderer747
@thebohemianwonderer747 5 жыл бұрын
It should be NEW modern spec wireing has to be used when any oven is installed re using old cable requires the cables resistence being confirmed which not every one can do , its also acceptable that a competent person can do this as long as the correct supply is provided and safety checks are perform before and after the install
@christopherebbs7714
@christopherebbs7714 2 жыл бұрын
Can I hardwire a plug in cooker to a 14 am wall switch
@LesLeckie
@LesLeckie 6 ай бұрын
I am replacing a 3,600Watt Neff oven with a 3,300Watt Neff oven. The existing oven was installed by a qualified electrician who installed a dedicated consumer unit for the purpose. Will I be able to transfer the connector from the old oven on the new one?
@heymrbassman
@heymrbassman 6 жыл бұрын
Hi, thanks for the information. I have a Zanussi single oven, rated 2.480 kw. Does this mean I can attach a 13 amp plug to it as the electrician left a socket behind where the oven is situated.
@Michael-zr9yl
@Michael-zr9yl 3 жыл бұрын
ha we just did and it popped the fuse, it needs to be into the oven only fuse
@finbarrdolan
@finbarrdolan 2 жыл бұрын
Will a modern stand alone single oven work off a 16 amp circuit or do you need to charge out the circuit breaker on the consumer unit for a 32 amp circuit breaker ? Thanks.
@ef7480
@ef7480 9 ай бұрын
The cable rating and size is more important than the 'circuit breaker'. Ib
@antdowling28
@antdowling28 5 ай бұрын
Can this oven be plugged into a double socket with a 13amp plug in induction hob or is it too many amps for a double socket?
@ianmarcho
@ianmarcho 6 жыл бұрын
Hi we want to install two Neff B57CR22N0B ovens above each other. Do we need an trim kit or something between the top of one and the bottom of the other or will they fit nicely to each other without a gap?
@thebohemianwonderer747
@thebohemianwonderer747 5 жыл бұрын
Trial fit both, if the top does touche the top edge of the bottom unit use that cheap hard boad to raise the top or upper unit ... Apperance is the factor most will pick up upon, if your stacking two singles youll need to line up the top of the upper oven with furniture doors but 1 ensure youve got the appropriate electrical outlets 2 ensure you create a ventilation route behind both units going up to the top of the cabinet they are in 3 plan the kitchen lay out , whats next to the oven units on both sides ... Keep fridges at least 200mm away from heat producing appliances it causes the fidge to overwork ...and shortens its life .
@raverhtid8966
@raverhtid8966 4 жыл бұрын
Are there any Oven/Hobs that you can plug into a 3 pin socket?
@jensschroder8214
@jensschroder8214 3 ай бұрын
Oven 3100W = 240V x 13A OK for a 3 pin plug. Hobs / Cookertop 7200W = 240V x 30A = 2x 230V x 16A = or Three-phase 400V: 2 hot wire a 16A to N; (Three-phase 230V 3 hot are need, no N, only old systems in Belgium)
@sorokolityuriy4508
@sorokolityuriy4508 10 ай бұрын
@daguch37
@daguch37 6 жыл бұрын
Thanks guys🤔
@dianac2847
@dianac2847 6 жыл бұрын
is the wattage based on bake mode for plug in or is broiler mode to be considered?
@mark5tytshort770
@mark5tytshort770 Жыл бұрын
Hi what size cable do you use for a fan oven to the plug 13amp,thanks
@badfairy9554
@badfairy9554 Жыл бұрын
4mm
@videoraver
@videoraver 6 жыл бұрын
Can this just be plugged in to a double socket on top of the worktop?
@VAX1970
@VAX1970 6 жыл бұрын
Not advisable, create a dedicated FCU spur from the ring
@thebohemianwonderer747
@thebohemianwonderer747 5 жыл бұрын
The answer is ... I would not advise you to do so 1 there could be damage caused to the electrical cable as it passes between the different materials along the route. 2 the heat could damage the cable if its too close ... It involves a cost but if you love your home and those in it get a sparkie to create a suitable electrical outlet
@craigk621
@craigk621 7 жыл бұрын
if you already have a hard wired cooker and replace it with one with a plug, what do you do with the existing hard wiring.?
@RuislipAppliances
@RuislipAppliances 7 жыл бұрын
Thanks for the question. You don't need to do anything with the existing wiring you can simply connect directly to the hard wiring. When you fit an oven that is rated to work on a 13amp plug it is always recommended the oven is hard wired with an isolation switch. I hope this helps.
@craigk621
@craigk621 7 жыл бұрын
+RuislipAppliances thank you. so best to get an electrician to take off the plug and attach the cable of the new oven to the existing hard wiring.
@RuislipAppliances
@RuislipAppliances 7 жыл бұрын
I would advise this is the best action for you to take.
@jonkeilty3340
@jonkeilty3340 6 жыл бұрын
RuislipAppliances my new hot point oven came with plug attached but on plate it says220-240v~50/60hz 3,65kw can I plug this in or does it need to be hard wired
@RuislipAppliances
@RuislipAppliances 6 жыл бұрын
Good afternoon, Thank you for your comment. 2 parts to this 1st the oven should not have arrived with a fitted plug. 2nd a 3.65Kw total connected load will need to be hard wired as this will draw 16amps.
@RuislipAppliances
@RuislipAppliances 4 жыл бұрын
We have listed Some ovens on our Website that are 13amp www.ruislipappliances.com/products.cgi?Search=13+amp
@patrickparker8417
@patrickparker8417 6 жыл бұрын
" Batteries not included " , oh boy welcome to the 21st century .
@MikFindersKeepers
@MikFindersKeepers 2 жыл бұрын
What type of wire will I require? .My oven manual states it can either be hardwired or plug in. I intend to plug in for now but eventually it will be hardwired. It’s a new oven but didn’t come with any wire. Would it be 13amp 3 core ? Does it need to be heat resistant? Thanks
@rachelhanford3934
@rachelhanford3934 4 жыл бұрын
Hi I have just purchased a Smeg 70cm dual fuel cooker it’s 3.0 kw can I use a plug or do I need it hard wired?
@rachelhanford3934
@rachelhanford3934 4 жыл бұрын
The model is C7GPX8 it does not say in any of the info we received and has a 2 foot wire coming out of the back with three wire like you would attach to a plug?? Can anyone help please?
@Drunk-le7pw
@Drunk-le7pw 4 жыл бұрын
Look at video at 1min 3w or over Hard wired.
@mikecoshan3752
@mikecoshan3752 3 жыл бұрын
Hi my old oven a Baumatic BO622SS (2000-2350W) is actually wired into a cooker point even though the user manual says it’s 13 amp. It has broken down and needs to be replaced under extended warranty . I have been given options for replacement Ovens which all come with a 13am cable. Please can you tell me if I need to get the cooker point changed to a 13amp socket
@leebrown3895
@leebrown3895 2 жыл бұрын
No you can hard wire it as long as the hard wiring is big enough to take the wattage,
@stephengerrard1120
@stephengerrard1120 3 жыл бұрын
My plug in oven is 3.5 kw is it suitable for hard wiring
@leebrown3895
@leebrown3895 2 жыл бұрын
has to be hard wired
@wearsider
@wearsider 5 жыл бұрын
We live in the 21 first century and need to get an electrician in the home to wire up the oven and hob. They send satellites into space, they have Rovers on Mars, and yet they are not capable of producing a higher voltage plugin system for a home appliance such as a oven. In Industrie they have high voltage connections or plugs for machines which are running day and night, if you told them when they bought the machine that it needed wired up to the wall, they would have laughed their bollocks off. Its 2019 not 1819 , people are inventing more complicated things than a plug to connect the oven. Someone could make a fortune if they did.
@Reg-th6zq
@Reg-th6zq 5 жыл бұрын
Well, you should make sure your 13Amp socket really does grip the plug. Its here where problems occur at full power. Plugs will get hot and over time you could get worse. You wont get this problem with hard wiring. If you use cheap sockets then expect problems. Have you ever felt the plug on an electric fire thats been on full power after an hour, hot.
@simonwtkns1
@simonwtkns1 3 жыл бұрын
I’m pretty sure that the huge drives they use in industry for rolling steel, don’t come with a socket on them. 🙄
@wearsider
@wearsider 3 жыл бұрын
@@simonwtkns1 Of course they don't, you are right and yet here in this country where I live, we still have to get an electrician to fix the oven to the wall, where there is a connection point, but its not a socket as such to plug in the oven with a simple plug, its a connection point with a connection to wire at least 5 wires from the oven to the wall and which an electrician is required to do, well so they say ;)
@simonwtkns1
@simonwtkns1 3 жыл бұрын
@@wearsider There’s a reason though. Household ring main sockets have a rating of 13amps maximum. That’s just about 3kW. That means anything above that cannot use the ring main. In write things are different. They tend to use spurs. Some of their connector types are rated more than 13amps subsequently. Please note, it’s not higher voltage. It’s higher current drawn from that same voltage. When I was a kid and we had new oven and it was supplied with a cable and a socket (alien to the UK). My father removed the socket and cable and replaced it with 40amp cable. For years I couldn’t understand how it could have possibly been safe to plug this oven in via a socket in Europe. It’s only on later years that I realised that in Europe both the cable and socket was rated higher than 13amps. However our system doesn’t exist for anything higher than 13amps and lower than 40amps, which was why we had to replace what looked like tiny cabling in comparison to the 40amp we had to use.
@paulwenman6933
@paulwenman6933 6 жыл бұрын
Recently bought Hotpoint oven rated 3.65kw but fitted with 13A moulded plug. This is to replace NEFF rated at 2.8kW which was hard wired with heavier gauge wires. Didn't make sense. Hotpoint replied that the rating plate states 3.65kW, but this on;y applies if all oven functions running at same time. They said this is not possible, hence adequacy of 13A plug. Make sense to anybody? What's the point of rating an oven above the full load that it could ever draw?
@RuislipAppliances
@RuislipAppliances 6 жыл бұрын
hi Paul, this is odd to say the least! , was it hotpoint themselves who said it? perhaps just ask them to put it in writing to you as your insurance company wants a copy to put on file next to your household policy, that usually focuses there attention....
@DerekHundik
@DerekHundik 5 жыл бұрын
I tell you more. These come with 1.5mm² flex cable. How it come then. You fitting 45A mcb for what ?
@DerekHundik
@DerekHundik 5 жыл бұрын
@@RuislipAppliances could you give me the link to that oven chart you mentioned
@romeo9017
@romeo9017 5 жыл бұрын
I need a wire connector please so I can move the oven without hard wiring it please?
@garylist9
@garylist9 4 жыл бұрын
My neff 2.9kw oven was wired into a 2.5mm cable and 20 amp breaker. It tripped more than once. Assume oven faulty. Any views. ?
@garylist9
@garylist9 4 жыл бұрын
Are you sure this oven can be 13 amp , my electrician has hardwired ?? Confused
@lumsdot
@lumsdot 3 жыл бұрын
Is the hob wired into the same cable
@richardforbes9700
@richardforbes9700 2 жыл бұрын
Depends on what else you've got on that circuit.
@VAX1970
@VAX1970 6 жыл бұрын
You should hardwire Neff Ovens into a FCU (Fused Connection Unit) with heat resistant flex (Type H05 V V-F or a higher rating). Only a licensed professional may connect the appliance. In the installation, there must be an all-pin isolating switch with at least 3 mm contact gap. This must remain accessible after installation, above the worktop.
@RuislipAppliances
@RuislipAppliances 6 жыл бұрын
Vax Buster hi, can you furnish me with a link to the regs that state this ?
@garylist9
@garylist9 4 жыл бұрын
Yep that's what it says in the instructions manual exactly I believe. So you would think best to follow that. My electrician came round fitted a 20 amp fuse connected my neff to this with 2.5 mm cable blah blah. After few tests the oven kept tripping. Although oven was brand new, I'd had it lying around for no. Of years. Gutted it didn't work. Any idea why didn't work ? The instructions don't explain in detail exactly how to fit the oven. I think the manufacturers give little info as they expect electrician to do it and, know what they doing. I'm having to presume oven is faulty.
@badfairy9554
@badfairy9554 Жыл бұрын
@@garylist9 hi a man from ao told me I could only have a cooker 20amp and needed 4mm cable. I have a 32amp fuse box/bourd can I have a cooker single oven 32 amp plus I have a hard cable thing in the wall. please help
@Giggler.
@Giggler. 11 ай бұрын
I wish this was a visual tutorial instead of a verbal 😢
@fallendevonish1869
@fallendevonish1869 Жыл бұрын
My oven just has a plug
@BenDover-ln6ns
@BenDover-ln6ns 3 жыл бұрын
Surely if the oven comes with a plug it’s good to go?
@brownwarrior6867
@brownwarrior6867 3 жыл бұрын
I think you might have totally misunderstood the entire point of this video. Some come with a plug,some need hardwired due to their higher rating than the 13 Amp a plug in is restricted to.
@BenDover-ln6ns
@BenDover-ln6ns 3 жыл бұрын
@@brownwarrior6867 Might have, so if there’s no plug you’ve got to hardwire it and if there’s a plug you plug it in. Unless I’m missing something then you plug in the plug, you wouldn’t attempt to take the plug off and hard wire it?
@nicky2591
@nicky2591 2 жыл бұрын
@@BenDover-ln6ns why carnt you hard wire it ,,who would want a plug in cooker ,when not enough plug sockets,wish they would keep everything the same ,it's just made my job of buying a cooker a lot harder,so now I have to look for one that doesn't have a bloody plug on
@elizabethcorven3599
@elizabethcorven3599 2 жыл бұрын
Thank you
Cooker Circuits Diversity, 15kW load, 32A circuit breaker.
22:29
NERF WAR HEAVY: Drone Battle!
00:30
MacDannyGun
Рет қаралды 33 МЛН
ROCK PAPER SCISSOR! (55 MLN SUBS!) feat @PANDAGIRLOFFICIAL #shorts
00:31
Integrated Oven Buying Guide   10 Things to Consider Before Buying an Oven
14:01
Neff B54CR71GOB Single Oven with Pyrolytic Cleaning
10:10
Lords Electrical
Рет қаралды 11 М.
Cable size Circuit breaker amp size How to calculate What cable
13:01
How to remove a built in oven, single or double
11:11
how-2-repair.com
Рет қаралды 373 М.
Neff B3ACE4HGOB Slide And Hide Single Integrated Oven
9:59
Lords Electrical
Рет қаралды 21 М.
Why are some Double ovens Built in and some built under?
3:07
RuislipAppliances
Рет қаралды 23 М.
"I Don't Like This!" Installing A Cooker Hob | Electrician Vlog
7:57
Eastway Electrical
Рет қаралды 27 М.
5 Mistakes Everyone Makes Changing Sockets ❌
11:44
Artisan Electrics
Рет қаралды 477 М.
小天使被小丑绑架,黑白天使救出小天使#short #angel #clown
0:39
Quando ACELERA eu faço MAIS GRANA 💰
0:16
Hermann Greb
Рет қаралды 36 МЛН
Think of stray animals 🙏😥
0:37
Ben Meryem
Рет қаралды 67 МЛН
Qual ELEMENTO é Melhor para ESCAPAR😱 #shorts
0:26
Lucan Pevidor
Рет қаралды 12 МЛН
Safe
0:16
OHIOBOSS SATOYU
Рет қаралды 6 МЛН
My little bro is funny😁  @artur-boy
0:18
Andrey Grechka
Рет қаралды 12 МЛН