Never Trust A Home Warranty Company!!

  Рет қаралды 74,457

HVAC Tech Tips

HVAC Tech Tips

Жыл бұрын

Went to a system not cooling and this is what I found! Has anyone ever seen a system run and cool like this?

Пікірлер: 223
@jericosha2842
@jericosha2842 Жыл бұрын
A lot of coils are compatible with both, just a different metering device
@Bear-cm1vl
@Bear-cm1vl Жыл бұрын
This one has a R410a TXV, as identified by the tag on the powerhead, so there is a mismatch no matter which refrigerant was used in it. I bet the loss of refrigerant is due to one or more leaks in the outdoor coil or condenser piping...
@sgoatr
@sgoatr Жыл бұрын
First company pancakes are 410 and 22 compatible. Yup just gotta change out the metering device to the correct size.
@christopherscott8853
@christopherscott8853 Жыл бұрын
Yeah, you just double the r-22 charge to actuate the stronger spring...lol.
@tedhicks5431
@tedhicks5431 Жыл бұрын
Goodman
@topnotchsir-c1166
@topnotchsir-c1166 11 ай бұрын
Piston metering device only
@marinermerrill3884
@marinermerrill3884 Жыл бұрын
I’ve seen home warranty companies do this a lot unfortunately
@mikefrommichigan9618
@mikefrommichigan9618 Жыл бұрын
Ive seen it 2 times where a guy actually filled a 22 system with 410a because the cost of 22 and its been running like that for 10 years.
@HVACTechTips
@HVACTechTips Жыл бұрын
That's crazy!
@MariosACandRefrigeration
@MariosACandRefrigeration Жыл бұрын
the relief on the compressor will open when it reaches over 100 deg.ambient.
@mikefrommichigan9618
@mikefrommichigan9618 Жыл бұрын
@MariosACandRefrigeration It's been 10 years and we don't really get 100 degrees in Michigan.
@MariosACandRefrigeration
@MariosACandRefrigeration Жыл бұрын
@@mikefrommichigan9618 LOL
@jaymz0074
@jaymz0074 Жыл бұрын
BS
@Rob-sn2ow
@Rob-sn2ow 4 ай бұрын
Leak search and repair + flush + replace condenser. You can make a great living by just going behind the ‘smart techs’😂. Sadly the home owners have no clue these hacks are doing this to them. Keep up the great work! Great videos! Sadly Integrity and pride in workmanship has become a rare trait in the trades it seems.
@johnmaranuk1842
@johnmaranuk1842 Жыл бұрын
Seen it before. As long as metering devices are correct and pressure adjusted accordingly.
@healthpeacelove80
@healthpeacelove80 Жыл бұрын
very true I did that to my home 4yrs ago and running like a champ
@ziads3653
@ziads3653 Жыл бұрын
Funny enough that’s how our unit is set up… superheat/subcooling is off like a mofo but I ended up adjusting my fan speed to get a good delta air temp and it’s been working for awhile now
@HVACTechTips
@HVACTechTips Жыл бұрын
Wow
@diomano.3341
@diomano.3341 Жыл бұрын
You might want to get that updated fam
@Threee_Eyez
@Threee_Eyez Жыл бұрын
😂
@Bear-cm1vl
@Bear-cm1vl Жыл бұрын
It's not long for this world, either due to compressor overheating/overamping, a tubing blowout due to excessive pressure near the test pressures of an R22 system and severely reduced system capacity.
@MegaDysart
@MegaDysart Жыл бұрын
I'm sure that's efficient lmao
@user-hb7qp3je9g
@user-hb7qp3je9g 11 ай бұрын
I’ve never done this but seen it done plenty of times at my last job. The science behind it is that Newer r22 scroll compressors come with Poe oil in them so you can use a r-22 replacement such as 427a, mo99, etc. this is the same oil that 410a systems use and the bypass head pressure for a r22 scroll compressor is 375. So some places instead of buying a 410a compressor will buy a r22 compressor and put it in a 410a system they’d do this to save a few hundred bucks. The units would run just fine but if the compressor ever went bad I’d replace it with the correct compressor.
@joecooksey4331
@joecooksey4331 Жыл бұрын
This just goes to show some HVAC dudes are 1,000% incompetent.
@angelosorio333
@angelosorio333 10 ай бұрын
Home warranty companies don’t have real techs , they got handy man 🤣
@angelosorio333
@angelosorio333 10 ай бұрын
This guy is a real tech , investigated the crime scene before getting his hands dirty
@kevinkrug466
@kevinkrug466 Жыл бұрын
You would be surprised how well a miss matched system like that will work. I mean it's not great but I have seen units just like that run for years
@ContinentalAC_Tom
@ContinentalAC_Tom 11 ай бұрын
Those home warranty companies are pirates 🏴‍☠️ with uniforms on 🤣 🤦‍♂️ they’re some people out there that just don’t care wtf they do .. smh …
@_n8787
@_n8787 Жыл бұрын
I know of a 410A system running 407C with an R22 TXV 😂 You can’t test the charge worth a shit but it cools great. Customer said just leave it as is.
@Sundog0811
@Sundog0811 10 ай бұрын
Ac guy literally just did this at my house. Told me that 407 is same as r22 pressure wise so will be fine. It has been working very well.
@petem6291
@petem6291 Жыл бұрын
Years ago when the auto industry switched from R-12 To R 134a when you went to class the instructor would explain all the reasons the two systems were incompatible. But the mechanic s that worked on fleets and taxi cabs would say they would just suck the old system out and add oil and recharge, I do believe them when they say the owners are not going to spend the money to do it right
@laker3
@laker3 11 ай бұрын
May not be the right thing to do, but I have seen this many times. They are compatible. That's why it's being done.
@P9rkour90
@P9rkour90 2 күн бұрын
Wow! Well that’s the beauty of the trade, you never know what you’re gonna run into
@Aaron-vv2hx
@Aaron-vv2hx Жыл бұрын
Compressor with r22 use mineral oil and r410 uses a poe oil.
@user-hb7qp3je9g
@user-hb7qp3je9g 11 ай бұрын
Majority of the newer r22 compressors come wit Poe oil already in them for retrofitting.
@alanhubbs7775
@alanhubbs7775 11 ай бұрын
I installed to r22 at the beach years ago. Maximum time on oceanfront about 10 years. Couldn't go back to replace them after rust out a condensers. I go back someone has replaced the outdoor condensers with r410 14 seer units. R22 evaporator coils liquid dryers not replaced pistons not replaced. Both lasted about three years until the evaporator coils began to leak. Both Goodman. Both units a liberally applied a anti-corrosive products. If I would have done it they have blown up on the first day.
@jorgegonzales6697
@jorgegonzales6697 11 ай бұрын
"I think you might want to look at replacement options." "Oh, you've got a home warranty? Say no more. I'm sure they will fix it like brand new!" 😂😂😂
@fastlife866
@fastlife866 Жыл бұрын
Iv done a few 410a coils but I removed the txv and put r22 txv in. Worked fine
@murkyturkey5238
@murkyturkey5238 Жыл бұрын
I might be wrong and I wouldn’t ever do it but I think you can use a 410a coil or txv with r22 but not the other way around, I wouldn’t do it but I think the pressures are the only difference
@nathantaylor1685
@nathantaylor1685 11 ай бұрын
Good thing is you only need to change the condenser now. Maybe want to find the leak, probably on a solder joint considering the air handler is new. But that compressor is deffinately damaged now.
@bryanharayda1975
@bryanharayda1975 11 ай бұрын
I’ve seen it work like that, but….the systems runs a low superheat because the 410-a valve opens farther than the R22 valve because of suction temp and design and yada yada. Low superheat at the compressor is the result
@rrcontracting9028
@rrcontracting9028 10 ай бұрын
You match the Freon to the expansion device . And make sure the oil is compatible . Things get sticky when it’s a heat pump .
@kevinroberts781
@kevinroberts781 10 ай бұрын
Bingo
@CapsCup2012
@CapsCup2012 10 ай бұрын
You can replace the txv with an r22 txv. It’ll work, I see it a lot in military housing
@BradMillsXRP
@BradMillsXRP 10 ай бұрын
I know what you’re saying I get it. But it worked for 20 years. So it had to provide some cooling, but I’ve only seen it on older equipment that uses a cap tube. And it cooled at a much lower capacity. How the compressor lasted. I will never know.
@adu-darkogabriel5697
@adu-darkogabriel5697 11 ай бұрын
thats normal to me just change the metering device or adjust it to 22a gas and you are good to go
@DanielHernandez-fx6df
@DanielHernandez-fx6df Жыл бұрын
I worked for a home warranty company, they ordered a new straight cool condenser 410A and told me to install it. I get to the residence and find the old system is a heat pump R22 only . I inform them that we need to replace the indoor coil as well. They told me to install the condenser and use my best judgment. There were so many situations at that company that didn’t sit right with me. I ended up leaving the company
@SpaceCadet327
@SpaceCadet327 Ай бұрын
That cu calls for a txv. Even says “indoor txv sub cooling 12*” right on the CU tag. I’ve really only seen them on a few old Lennox systems but they’re out there. That’s the wrong txv though so it would work but not efficiently. If they loaded it with 410 the it probably leaked somewhere at the CU. Whoever installed that ah screwed those people. When switching to 410 you should swap both units and replace or flush the lines depending on size and length. Quick fixes to get air almost always lead to even more costly repairs
@Hvacr123
@Hvacr123 11 ай бұрын
Ocean city Maryland we see that every week
@ianicus123
@ianicus123 Жыл бұрын
"working" and working, are two seperate things.
@FrenchBeefCDN
@FrenchBeefCDN 10 ай бұрын
My house was built in 09. Has an R22 condenser with a 410A Evap, piston. Uses R22. Got a 40f Evap with 15 degrees system superheat and about the same of subcooling. Probably rubbed out somewhere and lost the charge. I fix machines (commercial) that lost charge all the time. Change the drier, pull a long vacuum and recharge. I still use R22 if the customer wants to pay for it
@travisewing1795
@travisewing1795 5 ай бұрын
I’ve actually installed a R22 valve on a 4-10a system by accident of course due to me just being the green installer and I couldn’t get any more than a 10* delta
@againstallodds404
@againstallodds404 9 ай бұрын
I have an r22 2003 2.5 ton goodman. It has some leaks in the coils I was told that the coils have to be replaced and refill refrigerant or get a new package system😢.
@subcoolHVAC
@subcoolHVAC Жыл бұрын
I’ve seen R22 condensers work with R410a Air handlers w/TXV. Also seen R410a condenser w/ R22 txv Air handler which doesn’t work.
@philipedelstein2628
@philipedelstein2628 Жыл бұрын
Ni r22 is usually fixed orphace right ? 410 is what a txv is usually used for for the boiling temp pops it opened on demand
@tedhicks5431
@tedhicks5431 Жыл бұрын
Ive heard of it working. Then one of the guys at work accidentally put 410a in a 22 bard hp still running 4 yrs later i dont know
@jasonedwards4419
@jasonedwards4419 11 ай бұрын
Coils in condenser not set up for those pressures. Never mind the compressor.
@hankapana8237
@hankapana8237 10 ай бұрын
Haha seen it once myself. I couldn't believe it.
@theronrolle8732
@theronrolle8732 11 ай бұрын
Yes carry make ii were its compatible with both refrigerant
@vr6prodigy
@vr6prodigy Жыл бұрын
In the auto world, as long as you remove all traces of the previous refrigerant, you can run any refrigerant after that so long as the oils are still rated to protect the compressor. Which thankfully oils and metals haven't changed much, so oil really isn't the problem.
@kbrocco5965
@kbrocco5965 4 ай бұрын
Use to see that All the time doing warranty repairs.
@Bear-cm1vl
@Bear-cm1vl Жыл бұрын
Where did the refrigerant leak out? The leak location will suggest which refrigerant the system was recharged with and how extensive the additional damage is likely to be. I won't deal with home warranty companies, if for no reason than their attempts to bandaid systems until their coverage runs out, they can find a loophole to treat an issue as the subcontractor's responsibility or to say the repairs are outside the scope of their policy.
@thisisyourcaptainspeaking2259
@thisisyourcaptainspeaking2259 11 ай бұрын
Not without an R22 charge and expansion device. It also won't work with no charge.
@HygroHybrid
@HygroHybrid 7 күн бұрын
I've seen this a lot in Vegas.
@kylefry1342
@kylefry1342 11 ай бұрын
I’ve seen it about 4 times, and somehow it works for years. I think R22 on a 410 valve will work, although not correct, but 410 on an R22 valve definitely won’t work.
@AA-mg4fd
@AA-mg4fd Жыл бұрын
The min feed through a txv especially a ton and half txv is enough to cool the house usually. The puron TXv will push head pressure up a little but it will be below relief valve cutout
@jfjhtfghgfhgf
@jfjhtfghgfhgf 11 ай бұрын
Yes I’ve seen it and yes it will cool. But the only time I will do it. If it’s a piston r22 air handler and the condenser goes. I’ll put a 410a condenser on it and it runs perfect pressures everytime. And that’s only for someone whos really desperate and got low funds. Gives them 5 year parts on the condenser only.
@lorenzodamazeti4862
@lorenzodamazeti4862 10 ай бұрын
Cnn refill with r407 but must must do for vacuum complete
@jonsaircond8520
@jonsaircond8520 Жыл бұрын
Seen it many times as most guys that do a inside replacement never change the txv. Honestly for your average system it works ok is it right no does it work mostly yes. On that one I'd be more concerned about the lack of refrigerant. If it really bothers ya pop it out put a piston in and leave the valve for future use
@Pack044
@Pack044 25 күн бұрын
I know of 1 system running 410 with a r22 TXV right now lol
@user-nn5ph4js1n
@user-nn5ph4js1n Ай бұрын
My r22 unit runs a 410a coil with the right piston size it had a .67 before I used it
@SnowingNapalm
@SnowingNapalm Жыл бұрын
well after they steal the valuable r22 or assuming so by reading the label 🏷️ not the actual conversion ... they're usually disappointed at thier lesser quality refrigerant
@funnycuriosity7259
@funnycuriosity7259 Жыл бұрын
Well ,just put the half of r22 refrigeran and a half of r410a .😂😂😂😂
@josevela7868
@josevela7868 Жыл бұрын
😂😂😂😂
@stewy1031
@stewy1031 11 ай бұрын
I did it at my house put 005 carrier ahu 410 on a trane 15 xl flat top r 22 condenser . It's been heating and cooling fine for 7 years ++
@kevinroberts781
@kevinroberts781 10 ай бұрын
My R22 system has a txv. Works fine. Its from 2005
@joemomma7814
@joemomma7814 Жыл бұрын
Ive actually seen it work alot. Never efficiently, but it does cool. Used to do some work for a cheap apartment complex and they always wanted to supply the equipment when it failed so we just put it in the way they asked and told em no warranty. They also frequently had us install 410a heatpump condensers on 20 year old r22 air handlers. But they paid us good, and we had tons of service calls there to say the least! We tried telling them dozens of times that this is not right and its going to fail, but the stubborn maintenance supervisor thought he knew hvac better than someone who’s been doing it for 20 years lol. Oh well, more money in our pockets.
@rokashi2104
@rokashi2104 Жыл бұрын
Now the coil will have r22 oil in it , if you put r410 condeser will you clean the coil ? I saw a unit that outdoor was r410 with r22 coil with r22 txv worked ok for 10 years!
@timbyrne8514
@timbyrne8514 11 ай бұрын
All do is change the piston out side to match the txv. Retro fit
@suggesttwo
@suggesttwo Жыл бұрын
Wikipedia Transition from R-22 to R-410A Edit R-410A replaced R-22 as the preferred refrigerant for use in residential and commercial air conditioners in Japan, Europe, and the United States.[10][failed verification] Parts designed specifically for R-410A must be used, as R-410A operates at higher pressures than other refrigerants.[11] R-410A systems thus require service personnel to use different tools, equipment, safety standards, and techniques. Equipment manufacturers are aware of these changes and require the certification of professionals installing R-410A systems. In addition, the AC&R Safety Coalition has been created to help educate professionals about R-410A systems. R-22 Phaseout Edit In accordance with terms and agreement reached in the Montreal Protocol (The Montreal Protocol on Substances That Deplete the Ozone Layer), the United States Environmental Protection Agency has mandated that production or import of R-22 along with other hydrochlorofluorocarbons (HCFCs) be phased out in the United States. In the E.U. and the U.S., R-22 cannot be used in the manufacture of new air conditioning or similar units from 1 January 2010.[10] In other parts of the world, the phase-out date varies from country to country. All newly manufactured window air conditioners and mini split air conditioners in the United States come with R-410A.[12] Since 1 January 2020, the production and importation of R-22 has been banned; the only available sources of R-22 include that which has been stockpiled or recovered from existing devices.[10] R-410A use expanded globally and rapidly as it replaced R-22.[13]
@suggesttwo
@suggesttwo Жыл бұрын
Wikipedia
@robertdeneroy6067
@robertdeneroy6067 Жыл бұрын
R22 condenser will work with a 410a airhandler with txv but 410a condenser with r22 airhandler txv won't work
@markr78
@markr78 Жыл бұрын
R22 and 410 same coil for most companies the only thing that changes is the txv ,if they had 410 in the r22 condenser it will blow the condenser coil thats why it was empty
@Bear-cm1vl
@Bear-cm1vl Жыл бұрын
That TXV was tagged for R410a and has not been changed out, so even if the indoor coil is compatible with R22, the TXV will be underfeeding and giving less than 50% of the system's capacity at best. At worst, someone charged the system with R410a and the elevated pressures/compression ratio on the compressor would be blowing the internal relief, overheating the compressor and potentially blowing leaks in the R22 side of the system.
@AA-mg4fd
@AA-mg4fd Жыл бұрын
Smh the 410 would never reach "blow the coil over pressure" as the internal relief is under max operating pressure of that icp cond. Most likely a 22 yo unit cond coil started leaking because that happens.
@jamesrogers4674
@jamesrogers4674 11 ай бұрын
Don't know why it wouldn't work? I have an extremely Frankensteined system that's been operating flawlessly for 5 or 6 year's now. Didn't realize prices were about to shoot to the moon.
@jaysheat631
@jaysheat631 10 ай бұрын
Yes seen it a few times, worked but not efficiently
@edgarortiz2542
@edgarortiz2542 10 ай бұрын
Yup, dun it before. It works
@diegojh4004
@diegojh4004 11 ай бұрын
If they had a piston, you could switch it out to a 410 from an R 22 I was always told not to mix them especially with the newer units
@johnbartlett8780
@johnbartlett8780 Жыл бұрын
I had a 13yr r22 system that had a r410 evaporator I don't know how it ran so long
@Jugc0006
@Jugc0006 10 ай бұрын
They for got to remove the metering device to the right refrigerant. The coil can handle it.
@FoolOfATuque
@FoolOfATuque Жыл бұрын
NFIP only covered the condenser units of my brother in laws house after a flood. He had the sense to pay for new air handlers to match the new refrigerant though.
@locutz
@locutz 10 ай бұрын
My supervisor told me you can put 22 in a 410 system but you cant for some reason put 410 in a 22 system
@chrismiles8225
@chrismiles8225 Жыл бұрын
I've seen that same deal but not sure if it worked because I got the call to go troubleshoot. It was not functioning properly when I showed up.
@terrysookhoo2528
@terrysookhoo2528 11 ай бұрын
It does work u need to adjust d valve
@melvinwillingham233
@melvinwillingham233 Жыл бұрын
I’ve seen it. Had to correct it
@MyMessage_Is_Simple
@MyMessage_Is_Simple 10 ай бұрын
6th week of 2003 it was manufactured
@justinmartin431
@justinmartin431 10 ай бұрын
It happens all the time. It somehow cools for a while lol. Just not well
@donaldpainter956
@donaldpainter956 11 ай бұрын
Ive seen brand new 410a condenser unit on old r22 indoor coil several times it will blow the coil apart on the ends
@jbsimmons54
@jbsimmons54 Жыл бұрын
So what did you wind up doing in the end?
@dnell6854
@dnell6854 8 ай бұрын
There should be a way to stop this Madness!!!
@jerrywayne4887
@jerrywayne4887 11 ай бұрын
I worked on a Goodman split system with NO metering device at the evaporator! They said it had been cooling! 😂
@Daren954
@Daren954 11 ай бұрын
Then you have not worked on many home warranty services jobs. Because that is how home warranty companies fix a leaking evaporator coil. They only change out half of the system. Not the whole thing.
@michaelshanahan9578
@michaelshanahan9578 Жыл бұрын
Welcome to home warranty work... People always think they're going to get a free system from their home warranty company 🤣😂🤣
@ELLOSEE
@ELLOSEE 10 ай бұрын
Yes and Nope ..not gonna wk as set up cuz the txv gonna try and meter as if 410a ..not gonna wk as efficient as it should
@rolac6109
@rolac6109 Жыл бұрын
Should’ve said “that ain’t right !!” 😂😂 like gold.star.inspections says
@Henry-Hormin
@Henry-Hormin 10 ай бұрын
Indoor coil that model are really bad they leak bottom joints Replace everything 😅
@Raider352
@Raider352 10 ай бұрын
I would never purchase a home warranty.
@alysesands6456
@alysesands6456 9 ай бұрын
Home warranty companies don't visit properties.
@deanpippin
@deanpippin 11 ай бұрын
See it all the time in some apartments we have acquired the service on. They work but not the best.
@JonathanLukemusic
@JonathanLukemusic Жыл бұрын
Yes i have seen it work multiple times
@That_ac_dude
@That_ac_dude Жыл бұрын
They probably dumped the 22 and dropped 410a in the condenser.
@97Napkins
@97Napkins Жыл бұрын
Cannot work with r410 txv. Maybe put in a r22 piston and charge it up but I don't do work like that. Others will charge a r10a condenser with 407c and feel good about it 😂
@jameswaymyers6359
@jameswaymyers6359 11 ай бұрын
Yes it does work. It won't be efficient at all, seen it bro
@tractorboy31
@tractorboy31 Жыл бұрын
Ok. I know different refrigerant types but how bad is that and why. I honestly dont know anything about ac systems
@iwenive3390
@iwenive3390 Жыл бұрын
It will flood. Never have superheat and beat the compressor
@javi3167
@javi3167 8 ай бұрын
How does the valve know it’s 410a
@deebo_srt1513
@deebo_srt1513 11 ай бұрын
Will work fine when is the other way around is where you will se lot of problems
@stephenotto2294
@stephenotto2294 11 ай бұрын
Yeah seen it plenty
@priscillamacias1580
@priscillamacias1580 11 ай бұрын
Yes I have installer work
@frankpirate6708
@frankpirate6708 Жыл бұрын
I’ve seen it both ways
@tmacgee1234
@tmacgee1234 Жыл бұрын
Get 1 of those a year, rarely twice a year
@quentindavis6
@quentindavis6 11 ай бұрын
I’ve seen that several times already. Where is the compressor out quicker but it will work.
@CharlesLease-ei1ee
@CharlesLease-ei1ee Жыл бұрын
Do you know there’s gonna be people that’s gonna try this they don’t have the money to replace one but they got it either free or at a cheap price. They had the gas they’re going to do a test to see if it will work that’s what Americans do they tinker
@martinheatingcoolingmartin4693
@martinheatingcoolingmartin4693 11 ай бұрын
That’s crazy. Low on charge, no it’s not going to work. But, the mix matched equipment. No, I can’t see that it would have worked. Obviously who would ever try it! At least change the TXV.
@saltwateramateur9903
@saltwateramateur9903 Жыл бұрын
I have installed a evap on old r22 you just need to adjust the txv it works almost perfectly
@That_ac_dude
@That_ac_dude Жыл бұрын
I believe these carrier txvs aren’t adjustable.
@tedhicks5431
@tedhicks5431 Жыл бұрын
That txv bulb sensing temp doesn't care you cant do it the other way 410a on r22 txv it will not open
3 Things HVAC Contractors Don't Want You To Know About.
13:17
The DIY HVAC Guy
Рет қаралды 2,2 МЛН
Вечный ДВИГАТЕЛЬ!⚙️ #shorts
00:27
Гараж 54
Рет қаралды 14 МЛН
ТАМАЕВ УНИЧТОЖИЛ CLS ВЕНГАЛБИ! Конфликт с Ахмедом?!
25:37
Жайдарман | Туған күн 2024 | Алматы
2:22:55
Jaidarman OFFICIAL / JCI
Рет қаралды 1,8 МЛН
The Best Home Warranty Companies (From Worst to Best) | PissedConsumer
11:46
Locked Compressors
20:13
HVAC School
Рет қаралды 107 М.
Are home warranties really worth the money?
3:35
ABC 7 Chicago
Рет қаралды 13 М.
THEY SAID PLEASE HURRY THE AC'S ARE NOT WORKING
45:53
HVACR VIDEOS
Рет қаралды 260 М.
Should you buy a Home Warranty?  Pros and Cons!
10:39
Audra Lambert, Realtor
Рет қаралды 6 М.
HVAC Service Call | Easy Money!#hvacguy #hvaclife
10:41
HVAC GUY
Рет қаралды 9 М.
The #1 Cause Of Blown Fuses | Service Call
11:47
HVAC Tech Tips
Рет қаралды 15 М.
3 PROVEN Methods To Getting Colder Air From HVAC Vents.
10:45
The DIY HVAC Guy
Рет қаралды 349 М.
HVAC warranty is NOT what you think!
10:21
Atlas AC
Рет қаралды 32 М.
原来小蚂蚁会魔法?#火影忍者 #佐助 #家庭
0:17
火影忍者一家
Рет қаралды 1,1 МЛН
Очень ждал свою маму 💔
0:56
Awesome Cuts
Рет қаралды 2,7 МЛН
В семье появился подросток!
0:15
Victoria Portfolio
Рет қаралды 3,9 МЛН
WHAT’S THAT?
0:27
Natan por Aí
Рет қаралды 5 МЛН
Всегда проверяйте зеркала
0:21
Up Your Brains
Рет қаралды 10 МЛН